  #1  
Old 12/22/2007, 11:41 AM
4everwet 4everwet is offline
Registered Member
 
Join Date: Dec 2005
Location: oklahoma
Posts: 129
electrical advice needed

I'm running electric to my new fishroom which is located in the garage. I have a 150amp main and installed a 100amp breaker in the main panel, then ran 4/3 wire over to a 100amp subpanel for the fishroom. I then plan to run 4 20amp circuits. My question is am I on the right track here? Will the 150amp main be ok? All my house appliances are gas so I would think the load from the house is minimal anyway. Any help greatly appreciated!
  #2  
Old 12/22/2007, 12:23 PM
j_electric j_electric is offline
Registered Member
 
Join Date: Apr 2007
Location: Vista Ca,
Posts: 22
4/3 is pushing it on a 100 amp breaker
4/3 is good to about 85 amps
I would change the breaker to 60 amps and that is more then plenty for 4 20amp circuts
if you are ru7nning a large pump for return or a CL try to make them 220v they will run better and more energy efficiant

-joe
  #3  
Old 12/22/2007, 01:49 PM
46bfinGA 46bfinGA is offline
Registered Member
 
Join Date: Mar 2005
Location: Ball Ground, Ga.
Posts: 910
I would definately agree.
  #4  
Old 12/22/2007, 04:19 PM
Elliott Elliott is offline
Premium Member
 
Join Date: Dec 2001
Location: Scottsdale, AZ
Posts: 1,088
Quote:
Originally posted by j_electric
4/3 is pushing it on a 100 amp breaker
4/3 is good to about 85 amps
I would change the breaker to 60 amps and that is more then plenty for 4 20amp circuts
if you are ru7nning a large pump for return or a CL try to make them 220v they will run better and more energy efficiant

-joe
I'm curious how 220v runs more energy efficient, can you explain it in non electrician language? lol thanks
__________________
"Try not to become a man of success but rather a man of value" Albert Einstein
  #5  
Old 12/22/2007, 04:35 PM
azrednex azrednex is offline
Ruger dog
 
Join Date: Jun 2006
Location: Chandler, AZ
Posts: 1,162
Elliot, in non-electrical but still somewhat scientific terms, amps and volts are inversely proportianate, and amps can be read "energy" when your thinking efficiency.

BTW I don't remember specifically but I think I have 4/3 to my 100 amp sub in my own garage.
__________________
90g SPS
90g LPS
30g planted FW community tank
  #6  
Old 12/22/2007, 05:00 PM
Elliott Elliott is offline
Premium Member
 
Join Date: Dec 2001
Location: Scottsdale, AZ
Posts: 1,088
Quote:
Originally posted by azrednex
Elliot, in non-electrical but still somewhat scientific terms, amps and volts are inversely proportianate, and amps can be read "energy" when your thinking efficiency.

BTW I don't remember specifically but I think I have 4/3 to my 100 amp sub in my own garage.
so with a higher voltage (220v) you use less amps (energy)?
__________________
"Try not to become a man of success but rather a man of value" Albert Einstein
  #7  
Old 12/22/2007, 05:10 PM
azrednex azrednex is offline
Ruger dog
 
Join Date: Jun 2006
Location: Chandler, AZ
Posts: 1,162
Correct, I remember a motor that used something like 16 amps at 120v but, when I switched it to 220-240v it dropped to 10a or so.
__________________
90g SPS
90g LPS
30g planted FW community tank
  #8  
Old 12/22/2007, 05:17 PM
Elliott Elliott is offline
Premium Member
 
Join Date: Dec 2001
Location: Scottsdale, AZ
Posts: 1,088
thanks azrednex
__________________
"Try not to become a man of success but rather a man of value" Albert Einstein
  #9  
Old 12/22/2007, 05:34 PM
azrednex azrednex is offline
Ruger dog
 
Join Date: Jun 2006
Location: Chandler, AZ
Posts: 1,162
No problem.
__________________
90g SPS
90g LPS
30g planted FW community tank
  #10  
Old 12/22/2007, 08:38 PM
NewBostonConst NewBostonConst is offline
Registered Member
 
Join Date: Jul 2007
Location: Mi
Posts: 8
You are supposed to run a 4 conductor for 220vac subpanel and put in a new ground rod. Most subpanels are 220vac. Running a 220vac panel will help you balance the load on your main panel also. If you run it 110vac you will end up having all the load on one leg of the power feed coming into your house, which isn't a good thing.

You will have to "unbond" the subpanel to install it correctly. If you are getting this inspected the things I am saying will be a requirement. If you aren't getting it inspected you can probably get it running, but not correctly.

1st wire is for L1 (one side of the main)
2nd wire is for L2 (other side of the main)
3rd wire is for Neutral
4th wire is for Ground

I did a quick search and found this. I didn't read it, but it may help.

http://www.electrical-online.com/sub...stallation.htm

Last edited by NewBostonConst; 12/22/2007 at 09:37 PM.
  #11  
Old 12/22/2007, 09:53 PM
dinge dinge is offline
Registered Member
 
Join Date: Nov 2007
Posts: 1
I have to disagree with azrednex. It is not because you have a higher voltage and lower Amps that you will have more power.

the formula for power is P= UxIxcos phi x root 3 ( for a 3 fase electric distribution ). So if you make voltage ( U ) higher then your Amps ( I ) can lower for the SAME power consumption.

The only gain you can have for it is that your wireing can be smaller in diameter ( directly linked to your Amp's ) so less expencive and your instalation will be less expencive as well for a surtain degree.
  #12  
Old 12/23/2007, 12:04 AM
j_electric j_electric is offline
Registered Member
 
Join Date: Apr 2007
Location: Vista Ca,
Posts: 22
Quote:
Originally posted by NewBostonConst
You are supposed to run a 4 conductor for 220vac subpanel and put in a new ground rod. Most subpanels are 220vac. Running a 220vac panel will help you balance the load on your main panel also. If you run it 110vac you will end up having all the load on one leg of the power feed coming into your house, which isn't a good thing.

You will have to "unbond" the subpanel to install it correctly. If you are getting this inspected the things I am saying will be a requirement. If you aren't getting it inspected you can probably get it running, but not correctly.

1st wire is for L1 (one side of the main)
2nd wire is for L2 (other side of the main)
3rd wire is for Neutral
4th wire is for Ground

I did a quick search and found this. I didn't read it, but it may help.

http://www.electrical-online.com/sub...stallation.htm


With the metioning of 4/3 this is a 4wire condutors 2-hots 1-neutral 1-ground , they label the wire this way because it is #4 wire with three conductors the ground is not counted as a conductor so for short they just call it 4/3

-joe
  #13  
Old 12/23/2007, 12:26 AM
Oldtimer Oldtimer is offline
Registered Member
 
Join Date: Oct 2001
Location: Grosse Pointe, MI
Posts: 51
I plan to run a subpanel in my fishroom fed by a double pole 60 amp breaker in the main panel. I'll have about 60' of wire in between the main and sub panels. I plan to have (4) 20 amp breakers in the sub panel. Max usage is expected to be 40 amps worst case, but generally closer to 30 amps. I planned to run 6/3 between the panels and an electrician confirmed this would be sufficient. Any disagreement here?
__________________
Building the Reef, One piece at a time.
  #14  
Old 12/23/2007, 02:21 AM
j_electric j_electric is offline
Registered Member
 
Join Date: Apr 2007
Location: Vista Ca,
Posts: 22
old timer that would be fine I typically runnig 6/3 at 50 amps but I over due everything #6 can run at 125% at 65 amps so your good

-joe
  #15  
Old 12/24/2007, 11:30 PM
4everwet 4everwet is offline
Registered Member
 
Join Date: Dec 2005
Location: oklahoma
Posts: 129
Is it required that I install those little fittings in the holes where the wires go thru the breaker panel?
  #16  
Old 12/25/2007, 09:51 AM
4everwet 4everwet is offline
Registered Member
 
Join Date: Dec 2005
Location: oklahoma
Posts: 129
????
 


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -5. The time now is 04:30 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef Central™ Reef Central, LLC. Copyright ©1999-2009