cgfi breakers keep tripping

I upgraded three 20 amp breakers to gfi breakers. The circuits were working fine and tested fine with ground tests.

Anyway, all three breakers tripped as soon as I restored power. I had to go around and unplug every single thing in every outlet to get them to reset.

Then, if I plug in any lamp, turn on any switch, they trip again. All three on three separate circuits.

Could I have three bad breakers? I did get them at Home Depot.

Thanks

Ryan.
  #2  
Old 01/06/2008, 07:50 PM
Riderxusa Riderxusa is offline
Registered Member
 
Join Date: Oct 2007
Location: Daytona Beach
Posts: 3
FishTruck, it sounds as if you may have installed them incorrectly. Highly unlikely you could have 3 "bad" breakers at the same time. How did you install them? The white wire on the breaker goes to to the neutral bar (the one in the panel that has a bunch of other whites, possibly some green or bare copper also) Then the white wire from the "3 circuits" is landed on the breaker, one white per breaker, usually there is a terminal screw just above the "curly" white wire on the breaker or has a dot of white paint. Keith
  #3  
Old 01/06/2008, 07:55 PM
FishTruck FishTruck is offline
Premium Member
 
Join Date: Jul 2007
Location: Downers Grove, IL
Posts: 232
WOOPS!

I hooked the curly white wire to the neutral bar and just moved the black, hot, wire from each circuit to the new breakers.

I did not go find the neutral wire from each circuit to put it on the new breakers. I just left them hooked to the neutral bar.

I guess this makes sense... I need the white wire from each circuit connected to each breaker and then each breaker grounded to the neutral bar...

I will re read the instructions.

Thanks so much.
  #4  
Old 01/06/2008, 08:37 PM
FishTruck FishTruck is offline
Premium Member
 
Join Date: Jul 2007
Location: Downers Grove, IL
Posts: 232
Bah! Shared neutrals on all circuits. Cannot use gfi breakers on this setup. Will have to go to the outlets.

Another one learned the hard way (at least not with a shock though).
  #5  
Old 01/07/2008, 04:53 PM
cannarella cannarella is offline
Registered Member
 
Join Date: Mar 2004
Location: Loganville, GA
Posts: 732
So there are not home runs for each circuit in the house? You should see where the romex comes into the circuit panel and follow the hot lead to the commone romex to identify it. I would like to know more of what you mean by shared neutrals.
__________________
If my phaser discharges off by as little as .06 terra watts, it would cause a cascading exothermal inversion.
  #6  
Old 01/07/2008, 06:00 PM
BeanAnimal BeanAnimal is offline
Premium Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 11,710
Re: cgfi breakers keep tripping

Quote:
Originally posted by FishTruck
I upgraded three 20 amp breakers to gfi breakers. The circuits were working fine and tested fine with ground tests.

Anyway, all three breakers tripped as soon as I restored power. I had to go around and unplug every single thing in every outlet to get them to reset.

Then, if I plug in any lamp, turn on any switch, they trip again. All three on three separate circuits.

Could I have three bad breakers? I did get them at Home Depot.

Thanks

Ryan.
GFCI breakers are NOT a real good idea for your fish tank. You would be much better off using the money to purchase several GFCI receptacles. You could get at least (9) for the price of the 3 breakers. Place (3) on each 20A branch circuit. That way a single faulting device does not bring other devices down with it.

With the GFCI breaker, any faulting device brings all of the other devices on that circuit down. This is not desirable
  #7  
Old 01/07/2008, 07:26 PM
RicGio RicGio is offline
Premium Member
 
Join Date: Oct 2002
Location: NJ
Posts: 508
I agree with Bean! Go with the GFCI outlets.
  #8  
Old 01/07/2008, 08:53 PM
kgross kgross is offline
Can't be listed on **
 
Join Date: Nov 1999
Location: Nampa, ID
Posts: 2,343
I agree with Bean also, with some more info. Many items will cause nuisance trips of GFI breakers, including many lighting systems and large pumps. You could end up with a full circuit tripping every time your lights come on.

Kim
__________________
America will only be the Land of the Free as long as it is the Home of the Brave.
  #9  
Old 01/07/2008, 09:25 PM
cannarella cannarella is offline
Registered Member
 
Join Date: Mar 2004
Location: Loganville, GA
Posts: 732
Yea, what Bean said.
__________________
If my phaser discharges off by as little as .06 terra watts, it would cause a cascading exothermal inversion.
  #10  
Old 01/07/2008, 10:43 PM
BeanAnimal BeanAnimal is offline
Premium Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 11,710
Who is this Bean cat anyway?
  #11  
Old 01/07/2008, 10:45 PM
kgross kgross is offline
Can't be listed on **
 
Join Date: Nov 1999
Location: Nampa, ID
Posts: 2,343
That is a good question we would all like to know who Bean is. I think he is the off screen version of Mr Bean...

Kim
__________________
America will only be the Land of the Free as long as it is the Home of the Brave.
  #12  
Old 01/07/2008, 10:54 PM
BeanAnimal BeanAnimal is offline
Premium Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 11,710
Nah... more like the off screen version of Mr. T


I pitty the fool...
  #13  
Old 01/07/2008, 11:08 PM
cannarella cannarella is offline
Registered Member
 
Join Date: Mar 2004
Location: Loganville, GA
Posts: 732
Oh sorry, I was going to start calling you Dr. House. I forgot.
__________________
If my phaser discharges off by as little as .06 terra watts, it would cause a cascading exothermal inversion.
  #14  
Old 01/08/2008, 06:52 PM
five.five-six five.five-six is offline
Premium Member
 
Join Date: Mar 2007
Location: Anaheim, California
Posts: 2,148
Quote:
Originally posted by FishTruck
Bah! Shared neutrals on all circuits. Cannot use gfi breakers on this setup. Will have to go to the outlets.

Another one learned the hard way (at least not with a shock though).
you can use GFI breakers, is your system single phase or 3 phase? just make sure you are sitting down when you see the price is your system wired in type NM THHN? if not you you are probably have flex, either way a GFI receptacle is cheaper and easier. if you are having "nuisance trips" then you have a problem that needs to be addressed. GFIs don't just trip for no reason
__________________
A free people ought not only to be armed and disciplined but they should have sufficient arms and ammunition to maintain a status of independence from any who might attempt to abuse them G.Washington
  #15  
Old 01/08/2008, 07:44 PM
kgross kgross is offline
Can't be listed on **
 
Join Date: Nov 1999
Location: Nampa, ID
Posts: 2,343
Many items can cause "nuisance trips" Cap start motors, Cap start lighting systems. When the cap is first charging the current in does not equal the current out so the gfi trips. That is why refrigerator circuits do not have to be GFI in the NEC .
__________________
America will only be the Land of the Free as long as it is the Home of the Brave.
  #16  
Old 01/08/2008, 07:45 PM
kgross kgross is offline
Can't be listed on **
 
Join Date: Nov 1999
Location: Nampa, ID
Posts: 2,343
Many items can cause "nuisance trips" Cap start motors, Cap start lighting systems. When the cap is first charging the current in does not equal the current out so the gfi trips. That is why refrigerator circuits do not have to be GFI in the NEC .
__________________
America will only be the Land of the Free as long as it is the Home of the Brave.
  #17  
Old 01/08/2008, 08:07 PM
slathrum slathrum is offline
Registered Member
 
Join Date: Jan 2006
Location: kansas
Posts: 17
It is very common for home runs to share a neutral. Most homes have two 120 volt phases coming in, and two circuits not on the same phase can share a neutral. The Romex used would basically have two hots, a neutral and a ground.
__________________
"Don't steal - the government hates the competition"
  #18  
Old 01/08/2008, 09:55 PM
BeanAnimal BeanAnimal is offline
Premium Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 11,710
I rarely see it in residential wiring, other than in the (2) required kitchen small appliance circuits.

I see it in commercial all the time... (4) (6) or even (8) circuits on a common neutral. The neutral simply has to be sized to carry the worst case imbalanced load.
  #19  
Old 01/09/2008, 12:05 AM
funman1 funman1 is offline
Got Salt?
 
Join Date: Jan 2006
Location: Citrus Heights, CA
Posts: 2,939
Yeah I don't much see it in residential.
But I use it everyday in Commercial (One of my Day Jobs)

Most commercial stuff is 3 phase so we can have 3 hots share a neutral if "Phased" correctly.

We use a "Round Robin" which means: 1 White, and 3 DIFFERENT colors (Not green, white, or gray)

And a "Full Boat" is: 1 Green, 1 White, and 3 DIFFERENT colors (Not green, white, or gray)
__________________
"Sharks are naturally peaceful."
"How'd you get that nasty cut anyway?"
"A shark bit me."

Jack of all trades, and master of none.
~Steve~
  #20  
Old 01/09/2008, 12:26 PM
RicGio RicGio is offline
Premium Member
 
Join Date: Oct 2002
Location: NJ
Posts: 508
In data centers also. They oversize the neutral BIGTIME for unbalanced loads and harmonics from the lighting and Computer loads.
  #21  
Old 01/09/2008, 12:44 PM
BeanAnimal BeanAnimal is offline
Premium Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 11,710
I have a harmonics problem to deal with next week. It is burning up a LOT of equipment. We are going to put an analyzer on it next week and see just how bad it is.
 


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -5. The time now is 09:16 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef Central™ Reef Central, LLC. Copyright ©1999-2009